Changing existing bathroom fan/light wiring

Thread Tools
 
Old 02-22-2006, 09:12 AM
  #1  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Changing existing bathroom fan/light wiring

The builder installed a bathroom fan with a light in each bathroom where there is a tub/shower.

But they wired the light and fan together on one switch. So if we go into the bathroom to simply get a towel and turn on the light, the fan comes on with it.

My question is... I know you can wire these units (both are made by Broan), so that you can have the light on one switch, the fan on another.

But based on the instructions, I can't tell if I have to get into the attic to get after the wiring, of if I can get at things from the bathroom?

Does anyone know? I guess I can go look, but I was curious...
Old 02-22-2006, 09:14 AM
  #2  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Here are the instructions...

http://www.broan.com/ImageLibrary/br...s/99042996.pdf
Old 02-22-2006, 09:27 AM
  #3  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Yup you absolutely can. On page 3 there is the wiring schematic that shows how to wire it so you can have one switch for the fan and one for the light. You'll more than likely need to get into the attic to run another wire.

However, check out the switch first before you do that. Shut off the power to that circuit and pull the switch out of the wall. See if there are two sets of wires coming from the fan unit. They may have just run both sets to the single pole outlet. If so, it's as simple as getting a switch that can control both the fan and the light or go with two separate switches.
Old 02-22-2006, 09:53 AM
  #4  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
I'm replacing the two exhaust fans in my upstairs bathrooms with heat/fan/light models and I need to run new wiring and add one of these to control all three settings.

Old 02-22-2006, 11:49 AM
  #5  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Originally Posted by NSXNEXT
Yup you absolutely can. On page 3 there is the wiring schematic that shows how to wire it so you can have one switch for the fan and one for the light. You'll more than likely need to get into the attic to run another wire.

However, check out the switch first before you do that. Shut off the power to that circuit and pull the switch out of the wall. See if there are two sets of wires coming from the fan unit. They may have just run both sets to the single pole outlet. If so, it's as simple as getting a switch that can control both the fan and the light or go with two separate switches.

Thanks Neil. I seem to recall poking in there when I was painting the bathroom and didn't see anything that would lead me to believe it would be a simple change of a switch.

I'll keep you posted.
Old 02-22-2006, 11:55 AM
  #6  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Normally the builders get away with as little as possible.
Old 02-22-2006, 11:56 AM
  #7  
XOXOXOXOX
 
TLuscious's Avatar
 
Join Date: Oct 2005
Location: Land of Oz
Age: 48
Posts: 841
Likes: 0
Received 0 Likes on 0 Posts
not worth fixing you will have to redo drywall after finding the wires in the wall then spliting them. Can you just live with it.
Old 02-22-2006, 11:59 AM
  #8  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Originally Posted by TLuscious
not worth fixing you will have to redo drywall after finding the wires in the wall then spliting them. Can you just live with it.

How do you figure?

All the wires run through conduit. Shouldn't be a big deal at all.
Old 02-22-2006, 12:24 PM
  #9  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Originally Posted by TLuscious
not worth fixing you will have to redo drywall after finding the wires in the wall then spliting them. Can you just live with it.

Huh? It's an upstairs bathroom and he has an attic. All he has to do is climb up in the attic, trace the wire from the fan to the stud pocket it goes down and run another wire to the switch.

Splitting wires? Might wanna stay away from the electricity.
Old 02-22-2006, 01:33 PM
  #10  
Senior Moderator
 
GreenMonster's Avatar
 
Join Date: Aug 2002
Location: Swansea, MA
Age: 57
Posts: 35,218
Received 15 Likes on 7 Posts
Originally Posted by TLuscious
not worth fixing you will have to redo drywall after finding the wires in the wall then spliting them. Can you just live with it.
The men are talking here... don't you have something to do in the kitchen
Old 02-22-2006, 01:51 PM
  #11  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Originally Posted by GreenMonster
The men are talking here... don't you have something to do in the kitchen
Get in the kitchen and make me a sammich.
Old 02-22-2006, 02:15 PM
  #12  
XOXOXOXOX
 
TLuscious's Avatar
 
Join Date: Oct 2005
Location: Land of Oz
Age: 48
Posts: 841
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by NSXNEXT
Huh? It's an upstairs bathroom and he has an attic. All he has to do is climb up in the attic, trace the wire from the fan to the stud pocket it goes down and run another wire to the switch.

Splitting wires? Might wanna stay away from the electricity.
How was I to know that it was not in his post. We are are redoing my bathroom now and it was a mess. But, my house is probably a lot older than his (1925).

By the way I got a big sandwich right between my legs for you perv!
Old 02-22-2006, 02:19 PM
  #13  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Originally Posted by TLuscious
How was I to know that it was not in his post.



Originally Posted by Scrib
The builder installed a bathroom fan with a light in each bathroom where there is a tub/shower.

But they wired the light and fan together on one switch. So if we go into the bathroom to simply get a towel and turn on the light, the fan comes on with it.

My question is... I know you can wire these units (both are made by Broan), so that you can have the light on one switch, the fan on another.

But based on the instructions, I can't tell if I have to get into the attic to get after the wiring, of if I can get at things from the bathroom?

Does anyone know? I guess I can go look, but I was curious...
Old 02-22-2006, 02:23 PM
  #14  
XOXOXOXOX
 
TLuscious's Avatar
 
Join Date: Oct 2005
Location: Land of Oz
Age: 48
Posts: 841
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by NSXNEXT
Ok genius where exactly does it say he has access to his attic??
Old 02-22-2006, 02:30 PM
  #15  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Originally Posted by TLuscious
Ok genius where exactly does it say he has access to his attic??
Originally Posted by Scrib
But based on the instructions, I can't tell if I have to get into the attic to get after the wiring, of if I can get at things from the bathroom?
I'll assume he has access to the attic or he wouldn't have posted it. And even if he doesn't. he can do it without the demolition you are referring to.

Since he already has a wire from the switch to the fan, all he has to do is disconnect it from the switch, attach two more pieces of Romex to it and pull it up from the fan.
Old 02-22-2006, 02:34 PM
  #16  
XOXOXOXOX
 
TLuscious's Avatar
 
Join Date: Oct 2005
Location: Land of Oz
Age: 48
Posts: 841
Likes: 0
Received 0 Likes on 0 Posts
good luck looks like these blowhards have you all fixed up!
Old 02-22-2006, 02:36 PM
  #17  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Originally Posted by TLuscious
good luck looks like these blowhards have you all fixed up!

1 - Quit crapping up thread.
2 - Post something useful or get back in the kiddie pool.
Old 02-22-2006, 02:42 PM
  #18  
XOXOXOXOX
 
TLuscious's Avatar
 
Join Date: Oct 2005
Location: Land of Oz
Age: 48
Posts: 841
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by NSXNEXT
1 - Quit crapping up thread.
2 - Post something useful or get back in the kiddie pool.

got to have the last word dont you!
Im out.
Old 02-22-2006, 03:05 PM
  #19  
1919
 
Scottman111's Avatar
 
Join Date: Mar 2005
Age: 39
Posts: 21,467
Likes: 0
Received 162 Likes on 134 Posts
Hey Scrib, I guess they didn't pull a 3-wire Romex from fan to switch, did they? Odds are probably no, but we do this for a fan like this or for just a fan/no light just in case the owner wants to add a fan/light.

But a lot of builders don't do this I know. NSXNEXT has the right idea it sounds like, but I can't think of a reason to run two different peices of 2-wire Romex. Running one peice of 3-wire and sharing the neutral should work the exact same way. It's just a lot less work and less wire crowding your box.

And I'm just curious, do they have the wire behind the wall in conduit, or the wire in the attic? Or both?
Old 02-22-2006, 03:50 PM
  #20  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Everything is run in conduit, so it'll be no big deal to pull a new wire and add a double switch.

Conduit is code... No Romex.
Old 02-22-2006, 03:54 PM
  #21  
Senior Moderator
 
GreenMonster's Avatar
 
Join Date: Aug 2002
Location: Swansea, MA
Age: 57
Posts: 35,218
Received 15 Likes on 7 Posts
Originally Posted by TLuscious
By the way I got a big sandwich right between my legs for you perv!


I'm gonna tell your husband
Old 02-22-2006, 03:56 PM
  #22  
The Third Ball
 
Sarlacc's Avatar
 
Join Date: Sep 2002
Location: Los Angeles, Ca
Age: 45
Posts: 49,201
Received 4,852 Likes on 2,589 Posts
Can we ban that annoying card reading bitch?

Sweet on having conduit run through the house...thats the way to do it. Good Luck.
Old 02-22-2006, 04:52 PM
  #23  
Senior Moderator
 
GreenMonster's Avatar
 
Join Date: Aug 2002
Location: Swansea, MA
Age: 57
Posts: 35,218
Received 15 Likes on 7 Posts
Originally Posted by Scrib
Everything is run in conduit, so it'll be no big deal to pull a new wire and add a double switch.

Conduit is code... No Romex.
At least in IL it is... We can get away with romex in MA (well on existing stuff at least, don't know about new construction).
Old 02-22-2006, 07:16 PM
  #24  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
The news isn't good.

I checked the box, and it's only wired for a single pole... Hot and common coming in... Blue and black on the switch... Nothng else.

I'll have to get up in the attic to check things out at some point... and maybe start tearing out the drywall...



























Old 02-22-2006, 07:41 PM
  #25  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Just took the fan apart... Doesn't look like I'll have to get in the attic after all.

As suspected, the builder tied the light and fan together and brought the combined hot down to the post. All I need is another wire nut and a double switch... Running off to Home Depot to pick it up... Right after my business call with China.
Old 02-22-2006, 08:03 PM
  #26  
Senior Moderator
 
GreenMonster's Avatar
 
Join Date: Aug 2002
Location: Swansea, MA
Age: 57
Posts: 35,218
Received 15 Likes on 7 Posts
Old 02-22-2006, 09:12 PM
  #27  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
WTF... I only saw single and three-pole switches. And I got there with 30 seconds before they closed.

I have to figure out how a three-pole works... I'm confused.
Old 02-22-2006, 09:46 PM
  #28  
1919
 
Scottman111's Avatar
 
Join Date: Mar 2005
Age: 39
Posts: 21,467
Likes: 0
Received 162 Likes on 134 Posts
What are you confused about Scrib? I can prolly help
Old 02-22-2006, 09:51 PM
  #29  
1919
 
Scottman111's Avatar
 
Join Date: Mar 2005
Age: 39
Posts: 21,467
Likes: 0
Received 162 Likes on 134 Posts
Originally Posted by Scrib
Everything is run in conduit, so it'll be no big deal to pull a new wire and add a double switch.

Conduit is code... No Romex.
No Romex eh, what parts of the house is that in?
Old 02-23-2006, 07:32 AM
  #30  
Senior Moderator
 
GreenMonster's Avatar
 
Join Date: Aug 2002
Location: Swansea, MA
Age: 57
Posts: 35,218
Received 15 Likes on 7 Posts
Originally Posted by Scottman111
No Romex eh, what parts of the house is that in?
All of it... I had wondered why he put conduit up when he finished off his garage... The answer was, 'cause he had to... it's code...
Old 02-23-2006, 07:53 AM
  #31  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Originally Posted by Scottman111
What are you confused about Scrib? I can prolly help

I think I figured it out.

Right now, I have one switch. The hot (black) comes into the switch, and the fan/light wire (blue) is tied into the switch. Common runs up to the unit.

I need a double switch so that I can control the fan and light seperately. But I'm a bit confused on how the this would work.

I have no problem running another wire from the fan/light and seperating the sources. Right now the fan and light and tied together in the unit.

So let's say I get the two wires down into the box (Blue for the Fan, Red for the light)...

How do I wire these into a double switch?

Does the hot (black) go into one of the posts? Or do I need to run it into both posts on the switch? Following me? Does the black need to be pigtailed or jumped or can it be put into one?
Old 02-23-2006, 08:34 AM
  #32  
Three Wheelin'
 
Zippee's Avatar
 
Join Date: Mar 2004
Posts: 1,355
Likes: 0
Received 1 Like on 1 Post
Turn the power off at the breaker!!

Seperate the light and fan wires where they are connected together and run a second wire from the fan/light to the box. You now have two wires running to the ceiling-the blue one and the new one. Hook each of them up to a switch output so that one goes to the fan, the other to the light. (Usually blue is light).

Use the same source (black) for both switches. Some switches tie the input together internally, some need a jumper-it depends on what you have.

Turn the power back on and check for smoke.
Old 02-23-2006, 10:40 AM
  #33  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Originally Posted by Zippee

Use the same source (black) for both switches. Some switches tie the input together internally, some need a jumper-it depends on what you have.
Ok, that's where I was getting hung up. I'll figure it out.

Turn the power back on and check for smoke.
lol
Old 02-23-2006, 09:00 PM
  #34  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
I got it. Took twenty minutes. Was a piece of cake.
Old 02-23-2006, 09:03 PM
  #35  
Three Wheelin'
 
Zippee's Avatar
 
Join Date: Mar 2004
Posts: 1,355
Likes: 0
Received 1 Like on 1 Post
Originally Posted by Scrib
I got it. Took twenty minutes. Was a piece of cake.
Old 02-23-2006, 11:44 PM
  #36  
1919
 
Scottman111's Avatar
 
Join Date: Mar 2005
Age: 39
Posts: 21,467
Likes: 0
Received 162 Likes on 134 Posts
Sorry I wasn't around to help Scrib, this is the first time I've been on today. Glad you figured it out though.

And BTW, when are you gonna do that work in your living room? (adding some lights if I'm not mistaken)
Old 02-24-2006, 07:37 AM
  #37  
Administrator Alumnus
Thread Starter
 
Scrib's Avatar
 
Join Date: Oct 2001
Location: Northwest IN
Posts: 26,326
Received 131 Likes on 82 Posts
Originally Posted by Scottman111

And BTW, when are you gonna do that work in your living room? (adding some lights if I'm not mistaken)

I really don't know how I'm going to be able to do it cleanly. It really looks like too difficult a project to pull off correctly.
Old 02-27-2006, 02:00 PM
  #38  
1919
 
Scottman111's Avatar
 
Join Date: Mar 2005
Age: 39
Posts: 21,467
Likes: 0
Received 162 Likes on 134 Posts
Originally Posted by Scrib
I really don't know how I'm going to be able to do it cleanly. It really looks like too difficult a project to pull off correctly.
I guess you can always hire a professional, right? Or do you really want it done that bad? (from what I remember I doubt it would be cheap)
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
Acura9915
2G TL (1999-2003)
7
02-24-2020 01:27 PM
cycdaniel
1G TSX Performance Parts & Modifications
8
12-17-2019 10:58 AM
BoricuaTL
Car Parts for Sale
138
04-08-2016 01:08 PM
Oakes
Wash & Wax
9
11-12-2015 09:34 PM
Aleax
3G TL Problems & Fixes
2
09-11-2015 11:31 AM



Quick Reply: Changing existing bathroom fan/light wiring



All times are GMT -5. The time now is 12:29 AM.