Heat Load Calculation Question

We are in the process of getting quotes for a new A/C unit for our main server room and I'm in the process of calculating our heat load. My dumb question is:

For devices that have redundant power supplies, do I need to factor in the wattage of the second power supply? My gut instinct says no since the 2nd power supply is there for redundancy and not capacity, but I want to be absolutely sure.
Old 04-26-2012, 11:58 AM
  #2  
Drifting
iTrader: (1)
 
rza49311's Avatar
 
Join Date: Feb 2006
Location: Southern VA
Age: 45
Posts: 3,072
Received 8 Likes on 6 Posts
Originally Posted by thunder04
We are in the process of getting quotes for a new A/C unit for our main server room and I'm in the process of calculating our heat load. My dumb question is:

For devices that have redundant power supplies, do I need to factor in the wattage of the second power supply? My gut instinct says no since the 2nd power supply is there for redundancy and not capacity, but I want to be absolutely sure.
We recently added another unit to our server room(two wall mounted units now) and I wasn't fully involved but I'm pretty sure the HVAC didn't need the wattage. He only needed the total amperage on the circuit from the panel. Based on the total amps you can figure it out I believe. I also found this which may help.

http://community.spiceworks.com/topi...erver-heatload
Old 04-26-2012, 12:25 PM
  #3  
Sweet!
Thread Starter
iTrader: (1)
 
thunder04's Avatar
 
Join Date: Jul 2007
Location: Northern VA
Posts: 4,104
Received 80 Likes on 69 Posts
The people managing the project requested wattage, so that's what I'm giving them.

I've decided that I'm only going to account for the wattage of one power supply with devices that have redundant power supplies. Since power supply wattage ratings are at maximum output, we should be well under what the heat load calculations come out to.

I AM, however, going to round up to the nearest thousand watts. My calculations are roughing out to 17,623 watts...so 18k watts of equipment that we want in the room.

We have half of what used to be in there at another location because of cooling problems.
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
Rachel Lu
1G TSX (2004-2008)
3
09-27-2015 09:53 AM
mv01
1G TSX (2004-2008)
3
09-15-2015 10:36 AM
datadr
5G TLX (2015-2020)
6
09-12-2015 09:12 PM
Mike Bertram
2G TL (1999-2003)
9
09-10-2015 09:27 AM



Quick Reply: Heat Load Calculation Question



All times are GMT -5. The time now is 12:37 AM.