'Auto' Setting on Thermostat does not turn heat on

Old 01-14-2009, 06:53 PM
  #1  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
'Auto' Setting on Thermostat does not turn heat on

does anyone know how i can see what the problem is? when the stat is set on HEAT and 'AUTO' and i see the room temp is definitely lower than the set temp, nothing turns on...

if i set the stat to ON, i hear the fan blows... the air doesn't feel warm though... so i don't know if the burners kick on...

does anyone know how i can diagnose for a bad stat??? should i clean the components of dust???
Old 01-14-2009, 06:59 PM
  #2  
Team Owner
 
doopstr's Avatar
 
Join Date: Jan 2001
Location: Jersey
Age: 52
Posts: 25,324
Received 2,043 Likes on 1,132 Posts
ON is just fan, so yeah no heat.

Does you heater have a pilot light? Maybe it's out.
Old 01-14-2009, 07:07 PM
  #3  
Team Owner
 
doopstr's Avatar
 
Join Date: Jan 2001
Location: Jersey
Age: 52
Posts: 25,324
Received 2,043 Likes on 1,132 Posts
You can also try raising and lowering the temp setting past the current room temp to see if you here a click. Most digital thermostats click when they call for heat/air.
Old 01-14-2009, 07:07 PM
  #4  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
checked the pilot light.. it is on... and it seems like it is the only thing on... with the STAT set 'ON' and 'HEAT', the fan runs but i would expect to see all the burners on in addition to the pilot light...
Old 01-14-2009, 07:08 PM
  #5  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
Originally Posted by doopstr
You can also try raising and lowering the temp setting past the current room temp to see if you here a click. Most digital thermostats click when they call for heat/air.
its an old school round wall STAT... it is currently set wayy above the current room temp... would i hear the click at the stat or at the furnace???
Old 01-14-2009, 07:11 PM
  #6  
Team Owner
 
doopstr's Avatar
 
Join Date: Jan 2001
Location: Jersey
Age: 52
Posts: 25,324
Received 2,043 Likes on 1,132 Posts
Ok, round wall most likely has a blob of mercury inside it so no click. If you pop the lid off of the stat you can see the blob move around as you turn the dial. Sometimes there is a little flash when the mercury makes contact as the electric jumps. That's about my extent of my knowledge though

If your furnace is very old check for pilot light. I think anything recent won't have one though.
Old 01-14-2009, 07:44 PM
  #7  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
yeah the unit has to be about 30 yrs old.. it is an old american standard... i was thinking about replacing it yet since i haven't moved into the house yet... but i need to run the heat in the winter so the pipes don't burst... so if it is the stat that need to get changed, ill just replace it until im ready to move in and change the whole furnace...
Old 01-14-2009, 07:44 PM
  #8  
Senior Moderator
 
fsttyms1's Avatar
 
Join Date: Aug 2002
Location: Appleton WI
Age: 49
Posts: 81,383
Received 3,063 Likes on 2,119 Posts
On is just for the fan (some like to have it running all the time to move and filter the air), Auto turns it on when heat/ac is needed. Your Stat may be bad.
Old 01-14-2009, 07:52 PM
  #9  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
okay how do i test for a bad stat?
Old 01-14-2009, 07:53 PM
  #10  
Senior Moderator
 
fsttyms1's Avatar
 
Join Date: Aug 2002
Location: Appleton WI
Age: 49
Posts: 81,383
Received 3,063 Likes on 2,119 Posts
Run to HD and buy a cheap T-Stat and wire it up and see if the furnace fires up?
Old 01-14-2009, 07:55 PM
  #11  
Three Wheelin'
 
Zippee's Avatar
 
Join Date: Mar 2004
Posts: 1,355
Likes: 0
Received 1 Like on 1 Post
Originally Posted by fsttyms1
On is just for the fan (some like to have it running all the time to move and filter the air), Auto turns it on when heat/ac is needed. Your Stat may be bad.
^^ +1. The on/auto switch only controls the fan.

The lack of heat is another problem. Try setting the fan to auto, then set the thermo to a high temp. If the fan doesn't kick in within a couple of minutes the heater is not getting a "go" signal from the thermostat. Might check the connections on the back and see if you are getting power to the thermo.
Old 01-14-2009, 08:04 PM
  #12  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
i will rip it out tomorrow to check the connections... i searched online and it says to jump the R and W wire to test the heat??? not sure if there are any HVAC guys on here???
Old 01-15-2009, 07:46 AM
  #13  
Burning Brakes
 
'06 Arctic's Avatar
 
Join Date: Jan 2007
Location: Pittsburgh, PA
Age: 43
Posts: 879
Likes: 0
Received 6 Likes on 4 Posts
Does your furnace try to kick on at all when the stat is set on Auto and the dial is set above the current room temperature? If the furnace does try to kick on, but does not blow heat, the furnace itself may not be properly going through its purge cycle and tripping itself out on a safety. If the furnace does not try to start its purge cycle at all, I would say you have a bad stat. I found a lot of helpful information on http://forum.doityourself.com/when I was installing my humidifier. May find some more information & help on there.
Old 01-15-2009, 08:04 AM
  #14  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
Set the thermostat to the lowest setting.
You said you hear the heater come on so it's probably not the thermostat
Pop the cover off the front of the heater and see if it ignites.
If you hear the fan on but no flame chances are the ignitor or the thermocoupler is bad (no I'm not making this up).
Old 01-15-2009, 11:16 AM
  #15  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
it ended up being the thermostat... the fan would kick on when i have it set to 'ON' but the air was not warm... so i figured that the stat was not sending for heat which confirms why the pilot was on but the burners wouldn't fire up...

i took apart the thermostat and touched the 'RH' wire with the 'W' wire... left the fan on 'AUTO' and went down to the furnace... the burners were on and in a few mins the fan kicked on and the air was warm...

went to home depot early this morning and picked up a new digital programmable stat... installed and ready to go... i'll check back after i leave for work...

thanks everyone for your help... the temp inside the house dropped below 32oF overnight and i didn't want the pipes to burst...
Old 01-15-2009, 11:21 AM
  #16  
Team Owner
 
doopstr's Avatar
 
Join Date: Jan 2001
Location: Jersey
Age: 52
Posts: 25,324
Received 2,043 Likes on 1,132 Posts
Congrats on the repair. Amazing how this stuff always breaks on the coldest night of the month.
Old 01-15-2009, 11:24 AM
  #17  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
Originally Posted by '06 Arctic
If the furnace does not try to start its purge cycle at all, I would say you have a bad stat. I found a lot of helpful information on http://forum.doityourself.com/when I was installing my humidifier. May find some more information & help on there.
thanks.. it was exactly that...

and i never visited that website till now... it looks very useful...
Old 01-15-2009, 11:36 AM
  #18  
Senior Moderator
iTrader: (2)
 
NSXNEXT's Avatar
 
Join Date: May 2000
Location: where the weather suits my clothes
Age: 55
Posts: 27,921
Received 1,080 Likes on 661 Posts
And now with a programmable thermostat, you should be able to lower your energy costs. win/win
Old 01-15-2009, 11:40 AM
  #19  
Burning Brakes
 
'06 Arctic's Avatar
 
Join Date: Jan 2007
Location: Pittsburgh, PA
Age: 43
Posts: 879
Likes: 0
Received 6 Likes on 4 Posts
Glad to hear you found the problem busted pipes would have sucked. that forum has been pretty useful for a lot of my home improvement projects.
Old 01-15-2009, 11:45 AM
  #20  
Senior Moderator
Thread Starter
iTrader: (5)
 
KaMLuNg's Avatar
 
Join Date: Feb 2002
Age: 41
Posts: 15,510
Received 1,090 Likes on 767 Posts
Originally Posted by NSXNEXT
And now with a programmable thermostat, you should be able to lower your energy costs. win/win
i dunno how much it will be reduced.. i only keep the heat at 55oF since no one is in the house with it still being renovated... i just don't want the pipes to burst...

once i move in, i will prob shop around for a more updated model... this American Standard is dirt old and prob 30+ yrs old... it runs like a champ still but i am sure i will save alot more after updating to a newer one...

Furnace

CIMG3992.jpg

A/C unit

CIMG4007.jpg

so my next thread will prob be a poll of Carrier vs Trane...
Old 01-15-2009, 12:11 PM
  #21  
Senior Moderator
Regional Coordinator
(Mid-Atlantic)
iTrader: (6)
 
97BlackAckCL's Avatar
 
Join Date: Jan 2005
Location: ShitsBurgh
Age: 42
Posts: 92,111
Received 4,406 Likes on 3,018 Posts
Glad to hear you fixed the issue, my igniter went and I was without heat for 3 days, was also worried about my pipes bursting, thankfully got a new part in for cost, glad you got the issue figured out
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
rockyboy
2G RDX (2013-2018)
170
12-06-2022 02:29 PM
Bahamanurse1
2G TL (1999-2003)
17
09-10-2015 10:05 PM
braveheart
Car Parts for Sale
0
09-07-2015 08:12 AM
prox
5G TLX Problems & Fixes
6
09-01-2015 02:03 AM


Quick Reply: 'Auto' Setting on Thermostat does not turn heat on



All times are GMT -5. The time now is 03:21 PM.